What is the maximum current that a 32 KW, 480-volt generator can deliver to a load?

Study for the Independent Electrical Contractors (IEC) Year 2 Part 3 Test. Use flashcards and multiple choice questions with hints and explanations to prepare confidently. Get exam-ready now!

To determine the maximum current that a 32 kW, 480-volt generator can deliver to a load, you can use the formula for three-phase power, which is given by:

[ P = \sqrt{3} \times V \times I ]

Where:

  • ( P ) is the power in watts (W),

  • ( V ) is the voltage in volts (V),

  • ( I ) is the current in amperes (A).

First, convert kilowatts to watts:

32 kW = 32,000 W.

Next, since the generator is operating at a voltage of 480 volts, you can rearrange the formula to solve for current ( I ):

[ I = \frac{P}{\sqrt{3} \times V} ]

Now, substitute the values into the formula:

[ I = \frac{32,000}{\sqrt{3} \times 480} ]

Calculating ( \sqrt{3} ) gives approximately 1.732. Now insert that into the equation:

[ I = \frac{32,000}{1.732 \times 480} ]

[ I = \frac{32,000}{829.